Yep schreef :
Ik heb deze methode gebruikt, sinds de ingebruikname 3 jaar terug 1x herhaald; komende winter ook maar weer eens doen (ik balanceer verder niet)
nordkyndesign.com/assembling-a...e-marine-house-bank/
Vanaf punt (4) in deze procedure, gewoon met lab voeding met krokodillenklemmetjes op de terminals van de aangesloten cellen (maar batterij afgeschakeld).
Method 1: Charging and Balancing Cells Using a Regulated Power Supply Unit
…
(4)
Then, while standing by only, reconnect the cells and allow the voltage to rise up to 3.60V and stabilise for a few minutes; this normally takes little time and additional current, provided the cells were fully absorbed at the lower voltage. Whether you target 3.60V, 3.65V or even 3.70V is of no consequence or interest if you are actively monitoring the process, because these values are often reached seconds apart only.
(5)
Disconnect the PSU from the cells again and wait. The cells should hold above 3.50V for at least 30 minutes. If not, bring them up again and hold them for a little longer until they do. At 3.60V, you may need to insist a little more than if using 3.65 or 3.70 volts; that’s all.
Ik doe het iets anders, wel vanuit een zover mogelijk geladen toestand met de normale lader.
Per cel:
-labvoeding instellen op CV 3.65 V en stroom laten meten
-aansluiten op de te balanceren cel
-als stroom onder 1A zakt, overschakelen op CC 500 mA
-doorladen tot 3.65 V
—> als dit bereikt is voeding loskoppelen en controleren of onbelastte celspanning na 15 min nog hoger is dan 3.5 V zoja: klaar en door naar volgende cel. Zonee: nog even doorladen in CC mode.
Hier moet je uiteraard wel bijblijven…